New firmware likes to endless loops.
Just like to poll one device then goes into loop till the device gives up.

Logs are now working. unit is not rebooting all the time.

Offline cj

  • Hero Member
  • *****
  • Posts: 1252
  • Karma: +1/-0
Re: 614 firmware buggy
« Reply #1 on: July 03, 2009, 07:05:49 am »
It's normal that Vera re-tries to poll a node if this fails. It's retrying for about 5 time, then it gives up, marking the job as failed.
Are you telling that Vera it's polling a node indefinitely and this responds every time?
Can you try to post also pecific part from your log, where you can see this issue, or try to send a trouble report when this happens.
Note: you'll need to have Verbose logging activated from Advanced->Logs

Offline zmistro

  • Hero Member
  • *****
  • Posts: 966
  • Karma: +1/-0
Re: 614 firmware buggy
« Reply #2 on: July 03, 2009, 11:30:41 am »
That is exactly what Vera is doing. Kinda like an endless stress test.
DateTime    ID   Name   Created   Started   Completed   Duration   Runtime   Status   LastNote   Node   Device   NodeType   NodeDescription
07/03/09 8:03:08.540   4516   pollnode #3node 3 1 cmds   09-07-03 8:03:08   09-07-03 8:03:08   09-07-03 8:03:08   0.531891000   0.516945000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:03:18.511   4517   pollnode #3node 3 1 cmds   09-07-03 8:03:18   09-07-03 8:03:18   09-07-03 8:03:18   0.501954000   0.488882000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:03:28.541   4518   pollnode #3node 3 1 cmds   09-07-03 8:03:28   09-07-03 8:03:28   09-07-03 8:03:28   0.532602000   0.518827000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:03:38.561   4519   pollnode #3node 3 1 cmds   09-07-03 8:03:38   09-07-03 8:03:38   09-07-03 8:03:38   0.542576000   0.528926000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:03:48.560   4520   pollnode #3node 3 1 cmds   09-07-03 8:03:48   09-07-03 8:03:48   09-07-03 8:03:48   0.552061000   0.538897000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:03:58.521   4521   pollnode #3node 3 1 cmds   09-07-03 8:03:58   09-07-03 8:03:58   09-07-03 8:03:58   0.512581000   0.499151000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:08.540   4522   pollnode #3node 3 1 cmds   09-07-03 8:04:08   09-07-03 8:04:08   09-07-03 8:04:08   0.532007000   0.516658000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:18.500   4523   pollnode #3node 3 1 cmds   09-07-03 8:04:18   09-07-03 8:04:18   09-07-03 8:04:18   0.491842000   0.478116000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:28.520   4524   pollnode #3node 3 1 cmds   09-07-03 8:04:28   09-07-03 8:04:28   09-07-03 8:04:28   0.512005000   0.496626000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:38.540   4525   pollnode #3node 3 1 cmds   09-07-03 8:04:38   09-07-03 8:04:38   09-07-03 8:04:38   0.531927000   0.518081000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:48.500   4526   pollnode #3node 3 1 cmds   09-07-03 8:04:48   09-07-03 8:04:48   09-07-03 8:04:48   0.491890000   0.476776000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:04:58.530   4527   pollnode #3node 3 1 cmds   09-07-03 8:04:58   09-07-03 8:04:58   09-07-03 8:04:58   0.522127000   0.508649000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:05:08.561   4528   pollnode #3node 3 1 cmds   09-07-03 8:05:08   09-07-03 8:05:08   09-07-03 8:05:08   0.552387000   0.537317000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:05:18.531   4529   pollnode #3node 3 1 cmds   09-07-03 8:05:18   09-07-03 8:05:18   09-07-03 8:05:18   0.512487000   0.498856000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:05:25.782   4530   pollnode_wake #13node 13 2 cmdsnode 13 2 cmds   09-07-03 8:05:25   09-07-03 8:05:25   09-07-03 8:05:25   0.594894000   0.570258000   Successful   Successfully polled node   13   29   ZWaveBinarySensor   
07/03/09 8:05:26.023   4531   Wakeup done 13   09-07-03 8:05:25   09-07-03 8:05:25   09-07-03 8:05:26   0.828401000   0.226154000   Successful   Transmit was ok   13   29   ZWaveBinarySensor   
07/03/09 8:05:38.561   4532   pollnode #3node 3 1 cmds   09-07-03 8:05:38   09-07-03 8:05:38   09-07-03 8:05:38   0.542239000   0.527119000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:05:48.521   4533   pollnode #3node 3 1 cmds   09-07-03 8:05:48   09-07-03 8:05:48   09-07-03 8:05:48   0.512415000   0.499006000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:05:58.541   4534   pollnode #3node 3 1 cmds   09-07-03 8:05:58   09-07-03 8:05:58   09-07-03 8:05:58   0.532289000   0.517091000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:08.500   4535   pollnode #3node 3 1 cmds   09-07-03 8:06:08   09-07-03 8:06:08   09-07-03 8:06:08   0.492015000   0.478290000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:18.520   4536   pollnode #3node 3 1 cmds   09-07-03 8:06:18   09-07-03 8:06:18   09-07-03 8:06:18   0.511920000   0.496423000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:28.540   4537   pollnode #3node 3 1 cmds   09-07-03 8:06:28   09-07-03 8:06:28   09-07-03 8:06:28   0.531861000   0.517792000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:38.560   4538   pollnode #3node 3 1 cmds   09-07-03 8:06:38   09-07-03 8:06:38   09-07-03 8:06:38   0.551726000   0.536616000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:48.527   4539   pollnode #3node 3 1 cmds   09-07-03 8:06:48   09-07-03 8:06:48   09-07-03 8:06:48   0.521950000   0.508386000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:06:58.547   4540   pollnode #3node 3 1 cmds   09-07-03 8:06:58   09-07-03 8:06:58   09-07-03 8:06:58   0.532353000   0.517317000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:08.567   4541   pollnode #3node 3 1 cmds   09-07-03 8:07:08   09-07-03 8:07:08   09-07-03 8:07:08   0.552281000   0.539043000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:18.527   4542   pollnode #3node 3 1 cmds   09-07-03 8:07:18   09-07-03 8:07:18   09-07-03 8:07:18   0.512183000   0.497149000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:28.547   4543   pollnode #3node 3 1 cmds   09-07-03 8:07:28   09-07-03 8:07:28   09-07-03 8:07:28   0.532225000   0.518639000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:38.517   4544   pollnode #3node 3 1 cmds   09-07-03 8:07:38   09-07-03 8:07:38   09-07-03 8:07:38   0.502302000   0.487168000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:48.537   4545   pollnode #3node 3 1 cmds   09-07-03 8:07:48   09-07-03 8:07:48   09-07-03 8:07:48   0.521876000   0.508142000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:07:58.557   4546   pollnode #3node 3 1 cmds   09-07-03 8:07:58   09-07-03 8:07:58   09-07-03 8:07:58   0.541901000   0.526435000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:08.517   4547   pollnode #3node 3 1 cmds   09-07-03 8:08:08   09-07-03 8:08:08   09-07-03 8:08:08   0.501893000   0.488113000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:18.537   4548   pollnode #3node 3 1 cmds   09-07-03 8:08:18   09-07-03 8:08:18   09-07-03 8:08:18   0.521703000   0.506452000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:28.567   4549   pollnode #3node 3 1 cmds   09-07-03 8:08:28   09-07-03 8:08:28   09-07-03 8:08:28   0.552719000   0.517642000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:38.527   4550   pollnode #3node 3 1 cmds   09-07-03 8:08:38   09-07-03 8:08:38   09-07-03 8:08:38   0.512531000   0.504617000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:48.557   4551   pollnode #3node 3 1 cmds   09-07-03 8:08:48   09-07-03 8:08:48   09-07-03 8:08:48   0.542401000   0.528872000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:08:58.567   4552   pollnode #3node 3 1 cmds   09-07-03 8:08:58   09-07-03 8:08:58   09-07-03 8:08:58   0.551986000   0.536766000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:08.527   4553   pollnode #3node 3 1 cmds   09-07-03 8:09:08   09-07-03 8:09:08   09-07-03 8:09:08   0.511874000   0.498385000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:18.547   4554   pollnode #3node 3 1 cmds   09-07-03 8:09:18   09-07-03 8:09:18   09-07-03 8:09:18   0.531991000   0.516594000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:28.507   4555   pollnode #3node 3 1 cmds   09-07-03 8:09:28   09-07-03 8:09:28   09-07-03 8:09:28   0.491941000   0.478182000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:38.537   4556   pollnode #3node 3 1 cmds   09-07-03 8:09:38   09-07-03 8:09:38   09-07-03 8:09:38   0.521853000   0.506794000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:48.557   4557   pollnode #3node 3 1 cmds   09-07-03 8:09:48   09-07-03 8:09:48   09-07-03 8:09:48   0.542270000   0.528811000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:09:58.807   4558   pollnode #3node 3 1 cmds   09-07-03 8:09:58   09-07-03 8:09:58   09-07-03 8:09:58   0.792384000   0.777400000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:08.767   4559   pollnode #3node 3 1 cmds   09-07-03 8:10:08   09-07-03 8:10:08   09-07-03 8:10:08   0.752142000   0.738924000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:18.547   4560   pollnode #3node 3 1 cmds   09-07-03 8:10:18   09-07-03 8:10:18   09-07-03 8:10:18   0.532240000   0.517225000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:28.747   4561   pollnode #3node 3 1 cmds   09-07-03 8:10:28   09-07-03 8:10:28   09-07-03 8:10:28   0.732434000   0.719103000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:38.827   4562   pollnode #3node 3 1 cmds   09-07-03 8:10:38   09-07-03 8:10:38   09-07-03 8:10:38   0.812388000   0.797393000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:48.547   4563   pollnode #3node 3 1 cmds   09-07-03 8:10:48   09-07-03 8:10:48   09-07-03 8:10:48   0.531880000   0.517736000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:10:58.567   4564   pollnode #3node 3 1 cmds   09-07-03 8:10:58   09-07-03 8:10:58   09-07-03 8:10:58   0.552055000   0.536633000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:08.777   4565   pollnode #3node 3 1 cmds   09-07-03 8:11:08   09-07-03 8:11:08   09-07-03 8:11:08   0.762292000   0.748704000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:18.557   4566   pollnode #3node 3 1 cmds   09-07-03 8:11:18   09-07-03 8:11:18   09-07-03 8:11:18   0.542480000   0.527406000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:28.517   4567   pollnode #3node 3 1 cmds   09-07-03 8:11:28   09-07-03 8:11:28   09-07-03 8:11:28   0.502292000   0.488796000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:38.728   4568   pollnode #3node 3 1 cmds   09-07-03 8:11:38   09-07-03 8:11:38   09-07-03 8:11:38   0.712826000   0.697742000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:48.567   4569   pollnode #3node 3 1 cmds   09-07-03 8:11:48   09-07-03 8:11:48   09-07-03 8:11:48   0.552491000   0.538785000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:11:58.887   4570   pollnode #3node 3 1 cmds   09-07-03 8:11:58   09-07-03 8:11:58   09-07-03 8:11:58   0.872140000   0.856582000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:12:08.547   4571   pollnode #3node 3 1 cmds   09-07-03 8:12:08   09-07-03 8:12:08   09-07-03 8:12:08   0.532145000   0.518337000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:12:18.807   4572   pollnode #3node 3 1 cmds   09-07-03 8:12:18   09-07-03 8:12:18   09-07-03 8:12:18   0.792196000   0.776386000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:12:28.647   4573   pollnode #3node 3 1 cmds   09-07-03 8:12:28   09-07-03 8:12:28   09-07-03 8:12:28   0.632407000   0.619011000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:12:38.085   4577   getnodedetails 2   09-07-03 8:12:37   09-07-03 8:12:37   09-07-03 8:12:38   0.756426000   0.723790000   Successful                   
07/03/09 8:12:38.749   4578   version node 2   09-07-03 8:12:38   09-07-03 8:12:38   09-07-03 8:12:38   0.599276000   0.583949000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:39.479   4579   manufacturer node 2   09-07-03 8:12:38   09-07-03 8:12:38   09-07-03 8:12:39   0.715609000   0.701192000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:40.088   4580   multi ch ver node 2   09-07-03 8:12:39   09-07-03 8:12:39   09-07-03 8:12:40   0.595376000   0.581190000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:40.808   4581   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:40   09-07-03 8:12:40   0.707546000   0.598338000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:41.408   4582   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:40   09-07-03 8:12:41   1.299141000   0.592899000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:42.008   4583   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:41   09-07-03 8:12:42   1.890892000   0.592926000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:42.608   4584   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:42   09-07-03 8:12:42   2.482867000   0.593093000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:12:43.518   4585   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:42   09-07-03 8:12:43   3.384459000   0.902946000   Successful   Successfully got the response command   2   31   ZWaveController   
07/03/09 8:13:06.910   4587   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:56   09-07-03 8:13:06   26.759581000   10.596637000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:13:18.669   4588   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:13:06   09-07-03 8:13:18   38.511305000   11.732122000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:13:31.509   4589   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:13:18   09-07-03 8:13:31   51.342830000   12.813734000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:13:37.230   4575   pollnode_wake #2node 2 3 cmds   09-07-03 8:12:37   09-07-03 8:13:31   09-07-03 8:13:37   59.929065000   5.683107000   Failed   Cannot send command to node   2   31   ZWaveController   
07/03/09 8:13:44.770   4586   multi inst cmd 2   09-07-03 8:12:40   09-07-03 8:12:43   09-07-03 8:13:44   64.628030000   61.244759000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:13:57.490   4590   nameset node 2   09-07-03 8:13:44   09-07-03 8:13:44   09-07-03 8:13:57   12.674731000   12.661015000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:13:57.531   4574   conf_jh#2   09-07-03 8:12:37   09-07-03 8:12:37   09-07-03 8:13:57   80.243303000   80.205656000   Aborted   Failed at: Setting the name   2   31   ZWaveController   
07/03/09 8:14:20.848   4576   Wakeup done 2   09-07-03 8:12:37   09-07-03 8:13:57   09-07-03 8:14:20   103.540276000   23.310202000   Aborted   Transmit failed with code: 1   2   31   ZWaveController   
07/03/09 8:14:28.817   4591   pollnode #3node 3 1 cmds   09-07-03 8:14:28   09-07-03 8:14:28   09-07-03 8:14:28   0.802319000   0.794225000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:14:38.537   4592   pollnode #3node 3 1 cmds   09-07-03 8:14:38   09-07-03 8:14:38   09-07-03 8:14:38   0.522258000   0.508822000   Successful   Successfully polled node   3   16   ZWaveDimmableLight   
07/03/09 8:14:48.557   4593   pollnode #3node 3 1 cmds   09-07-03 8:14:48   09-07-03 8:14:48   09-07-03 8:14:48   0.541948000   0.526495000   Successf

Offline micasaverde

  • Hero Member
  • *****
  • Posts: 1666
  • Karma: +15/-1
Re: 614 firmware buggy
« Reply #3 on: July 03, 2009, 12:53:15 pm »
We just pushed up a 616 update.  This should address all the issues.  We took the stable 602, and just added the change necessary to work around the problem with the new batch of Schlage locks that require the PIN codes to be sent in a different format.