Author Topic: Trane Thermostat - changing modes: Normal / Run <-> Energy Saving (ESM)  (Read 1142 times)

Offline Aaron

  • Hero Member
  • *****
  • Posts: 1985
  • Karma: +61/-193
I've never gotten this to work - hoping someone knows how to fix this...

Example:
Manually set the TStat to ESM
Have a Vera scene, or use the Device to select Normal / Run
 ... nothing happens. It never changes the mode.

Anyone know hot to get Vera to change the mode?

Offline Aaron

  • Hero Member
  • *****
  • Posts: 1985
  • Karma: +61/-193
Re: Trane Thermostat - changing modes: Normal / Run <-> Energy Saving (ESM)
« Reply #1 on: August 13, 2015, 11:47:29 am »
No one can help!?

Offline RichardTSchaefer

  • Community Beta
  • Master Member
  • ******
  • Posts: 10091
  • Karma: +764/-143
Re: Trane Thermostat - changing modes: Normal / Run <-> Energy Saving (ESM)
« Reply #2 on: August 13, 2015, 04:12:59 pm »
It's not obvious ... but you can go into Energy Saving Mode with:

luup.call_action("urn:upnp-org:serviceId:SwitchPower1", "SetTarget" {newTargetValue=0}, ThermostateDeviceID);


And return to previous mode with:
luup.call_action("urn:upnp-org:serviceId:SwitchPower1", "SetTarget" {newTargetValue=1}, ThermostateDeviceID);

Basically you are treating the Thermostat as a Binary switch!